,"灵宝法院标准化机房改造项目清单",,

,,

,,

, ,"序号","设备名称","参数要求","数量","单位",,

, ,"1","机房装修系统",,

,,

,,

,"1.

01","不锈钢踢脚线","行标高25MM踢脚线,材质不锈钢","100","米",,

, ,"1.02","全钢抗静电地板","600*600*35(mm)HPLA级300125001*106-1*1010Ω1.0","162","O",,

, ,"1.03","铝微孔吊顶","600*600*0.8mm率微孔吊顶","126.720078125","O",,

, ,"1.04","墙面彩钢板","尺寸:1200*2800(mm),表面平滑美观,无需再装修,不集尘、易保养;

隔音率可达45dB,安静无声;

表面采用烤漆钢板,防火、防潮、防霉、耐酸碱、防静电;

","198","O",,

, ,"1.05","窗户改造","机房窗户密封改造,操作间窗户更换等处理.","9","个",,

, ,"1.06","机房照明灯","600*600规格LED照明灯","14","套",,

, ,"1.07","照明线缆","ZR-BV2.5,阻燃2.5平方铜芯电源线","4","盘",,

, ,"1.08","玻璃隔断处理","原有玻璃隔断框架拆除并现场制作安装,含门夹,把手等五金","1","次",,

, ,"1.09","机房防水处理","原有渗水墙面铲除并重新进行防水处理","1","项",,

, ,"2","机房配电与防雷接地系统",,

,,

,,

,"2.01","机房专用接地","包括镀锌扁铁、防雷连接器符合GB-50057094《建筑物防雷设计规范》(2000补充版)和GB-50147-93《计算机房防雷设计规范》要求,接地极电阻Q4欧姆","1","项",,

, ,"2.02","工业插头","国产三芯32A专用工业插头,符合行业标准","10","对",,

, ,"2.03","防雷PDU","机柜专用PDU机柜插座8位10A工业PDU插排3米","12","个",,

, ,"2.04","插座线缆","ZR-BV2.5,阻燃2.5平方铜芯电源线","6","盘",,

, ,"2.05","金属软管","G25规格金属软管","200","米",,

, ,"2.06","机房配电柜","定制机房配电柜,含配电模块.","1","套",,

, ,"2.07","机房电缆","YJV-4*25+1*16机房专用电缆,交联聚乙烯绝缘聚氯乙烯护套电力电缆4根25平方主线,1根16平方地线","100","米",,

, ,"2.08","机柜电缆","ZRRV3*6mm2,3根阻燃6平方机柜电缆","4","盘",,

, ,"2.09","铜皮","国产行标4*0.1铜皮","1000","米",,

, ,"2.1","扁铜","国产行标3*25mm扁铜","36","米",,

, ,"2.11","一级防雷器","相五线制电源第二级电涌保护器/通流量40KA(8/20us)/安装于楼层或机房配电箱前端","1","套",,

, ,"2.12","二级防雷器","单模块40KA,用于3线制供电系统的电涌保护器","3","套",,

, ,"3","机房新风与恒温恒湿系统",,

,,

,,

,"3.01","新风系统","对室外新风过滤,防尘,增加负离子,保护机房空气环境,避免灰尘过大影响设备运转,减少设备故障率.室内外双向换气,新风等量置换.过滤处理:新风过滤处理应符合建筑法规要求.过滤器需阻止灰尘和有害气体等污染物进入室内.高效节能要求:内置静止热交换器,热交换效率应大于70%,冷热负荷(室温)不受新风影响,大幅度降低新风处理所需能量,实现高效节能.","1","台",,

, ,"3.02","精密空调","总冷量(kW)≥20.0显冷量(kW)≥18.3风量(m3/h)≥6500显热比≥0.91冷风比≥3.8噪声(dB)≤55送风方式下送风加湿量(kg/h)≥5加湿方式≥电极式加热电加热(kW)≥6压缩机数量(台)1台室外风机节能环保EC风机","1","台",,

, ,"3.03","空调冷媒管","气管,液管采用直管安装,含保温棉及室内机、室外机连接电缆","22","米",,