1 ¤ Germany (0

91 87) 10-0 - USA (847) 827-7600 - UK (01296)

420336 - www.

e-t-a.com Issue F

77 Authority Voltage ratings Current ratings VDE, Semko AC

240 V, DC

28 V 0.1...20 A (EN 60934) DC

50 V 0.1...20 A double pole DC

50 V 0.1...10 A single pole LRoS, BV AC

250 V, DC

28 V 0.1...20 A UL, CSA AC

250 V, DC

50 V 0.1...20 A Voltage rating AC

240 V;

DC

50 V (AC

250 V UL/CSA) (AC

415 V to special order) Current ratings 0.1...20A(upto30Atospecialorder,singlepoleonly) Typical life 50,000 operations for IN ≤16 A double pole 30,000 operations for IN ≤16 A single pole, 10,000 operations for IN >16 A Ambient temperature -30...+60 °C (-22...+140 °F) Insulation co-ordination Rated impulse Pollution (IEC

60664 and

60664 A) withstand voltage degree 2.5 kV

2 reinforced insulation in operating area Dielectric strength (IEC

60664 and 60664A) Test voltage operating area AC 3,000 V between poles (2 pole) AC 1,500 V Insulation resistance >100 M? (DC

500 V) Interrupting capacity Icn 0.1...2 A

10 x IN 2.5...20 A

250 A

2 pole, or

150 A

1 pole Interrupting capacity IN UN

2 pole (UL 1077) 0.1...

2 A AC

250 V

200 A 2.5...

3 A AC

250 V 1,000 A 3.5...

8 A AC

250 V 2,000 A

9 ...

16 A AC

250 V 3,500 A 18...

20 A AC

250 V 5,000 A 0.1...20 A DC

50 V 1,000 A Degree of protection operating area IP

40 (IEC 60529/DIN 40050) (IP

54 with water splash protection) terminal area IP

00 Vibration

8 g (57-500 Hz), ±0.61 mm (10-57 Hz) to IEC 60068-2-6, Test Fc

10 frequency cycles/axis Shock

30 g (11 ms) to IEC 60068-2-27, Test Ea Corrosion

96 hours at

5 % salt mist, to IEC 60068-2-11, Test Ka Humidity

240 hours at

95 % RH, to IEC 60068-2-3, Test Ca Mass approx.

33 g (double pole) approx.

27 g (single pole) Packaging quantities: 20, 25, 35,

50 or

60 pcs depending on the version Thermal Overcurrent Circuit Breaker 3120-F7.. Description E-T-A's proven type

3120 in a new attractive styling (S-type TO CBE to EN

60934 with trip free mechanism) offering the choice of single pole, double pole with single pole protection, and double pole with protec- tion on both poles. Designed for snap-in panel mounting with illumina- tion as an option. Under overload conditions the rocker returns to the OFF position. Any one of the following additional function modules can be supplied factory fitted to the rear of the switch/circuit breaker. q Under voltage release coil (for double pole versions only). q Magnetic trip coil for short circuit protection. q Magnetic trip coil for remote relay trip. q Auxiliary contacts for status signalling. q Mechanical slide interlock. Approved to CBE standard EN

60934 (IEC 60934). Available accessories: water splash protection and actuator guard to prevent inadvertent operation. Technical data 3120-F7.. Approvals Current Internal rating resistance per (A) pole (?) 0.1

94 0.2

24 0.3

12 0.4 5.30 0.5 4.20 0.6 2.90 0.8 1.50

1 0.9 1.2 0.80 1.5 0.45

2 0.27 2.5 0.0785

3 0.0595 3.5 0.0565

4 0.0435 4.5 0.0435

5 0.0325

6 0.0215

7 0.0165

8 0.0165

10

下载(注:源文件不在本站服务器,都将跳转到源网站下载)