6 Bus bar protection
7 Fault record
8 Protection of reactive power compensation device 8.1 Power capacitor protection 8.2 Shunt reactor protection 8.3 Static reactive power compensation device protection
9 Current-limiting reactor protection
10 Motor protection
11 High-voltage inverter protection
12 Auto reclosing
13 Automatic transfer switching device of standby power
14 Load down device of auto low frequency and voltage
15 Synchronization concatenation
16 Auto regulated excitation and auto cut-off excitation 16.1 Auto regulated excitation 16.2 Auto cut-off excitation
17 Requirement on related circuit and equipment 17.1 Secondary circuit 17.2 Current transformer and voltage transformer 17.3 DC power 17.4 Cable and optical fiber cable 17.5 Interface and communication protocol 17.6 Grounding and anti-interference measures Appendix A Minimum sensitive coefficient of relaying protection
4 1. 总则 1.0.1 为在电力装置的继电保护和自动装置设计中, 贯彻执行国家的技术经济政策, 做到安全可靠、 技术先进、经济合理,制定本规范. 1.0.2 本规范适用于 3~110kV 电力线路和设备、单机容量为 60MW 及以下发电机、75MVA 及以下电 力变压器等电力装置的继电保护和自动装置的设计. 1.0.3 电力装置的继电保护和自动装置的设计,除应符合本规范外,尚应符合国家现行有关标准、 规范的规定.
5 2. 一般规定 2.0.1 电力设备和线路应装设反应短路故障和异常运行的继电保护和自动装置. 继电保护和自动装 置应能及时反应设备和线路的故障和异常运行状态,并应尽快切除故障和恢复供电. 2.0.2 电力设备和线路应有主保护、后备保护和异常运行保护,必要时可增设辅助保护. 2.0.3 继电保护和自动装置应满足可靠性、选择性、灵敏性和速动性的要求,并应符合下列规定:
1 对相邻设备和线路有配合要求时,上下两级之间的灵敏系数和动作时间应相互配合;
2 当被保护设备和线路在保护范围内发生故障时,应具有必要的灵敏系数;
3 保护装置应能尽快地切除短路故障.当需要加速切除短路故障时,可允许保护装置无选择性 地动作,但应利用自动重合闸或备用电源的自动投入装置缩小停电范围. 2.0.4 保护装置的灵敏系数,应根据不利正常运行方式和不利故障类型进行计算.必要时,应计及 短路电流衰减的影响.各类短路保护的最小灵敏系数,应满足附录 A 的要求. 2.0.5 数字式继电保护和自动装置应满足下列要求:
1 装置应具有自动在线检测、闭锁和装置异常或故障报警功能;
2 装置应具有方便的投入和退出功能.
3 装置在保护动作、告警等事件时,应有对应的事件记录,以便于运行人员处理和分析.
4 装置的开关量输入和输出当采用硬接点时应符合 DL/T 478―2013 的4.5.1 及4.5.2 要求. 2.0.5 智能变电站单间隔保护装置宜直接采样、直接跳闸.对于涉及多间隔的保护(如母线保护) 可采用网络跳闸方式,相关设备应满足可靠性和速动性的要求. 2.0.5 智能变电站保护装置宜采用集成装置,集成测控、计量等功能. 2.0.6 智能变电站备自投、自动低频低压减负荷装置等功能宜由变电站自动化系统实现,采用网络 采样、网络跳闸方式.
6 3. 发电机保护 3.0.1 电压在 3kV 及以上,容量在 50MW 及以下的发电机,对下列故障及异常运行方式应装设相应 的保护装置: